TMe
Gold Member
Offline
Posts: 787
I am evil Homer, I am evil Homer..!
|
 |
« on: August 04, 2008, 01:28 PM » |
|
I'd like to use my garage as a band practice space, but the power supply is only two-prong (ungrounded).
Is that going to cause problems for amps and small P.A.?
If so, is there any way to overcome the lack of grounding, other than rewiring the garage?
|
|
|
|
|
Logged
|
"Some people say I ain't so super groovy. Why don't I leave the music alone?" Black Uhuru
|
|
|
Bart Elliott
Chef de Cuisine
Platinum Member
Online
Posts: 12772
Be Thankful
|
 |
« Reply #1 on: August 04, 2008, 02:06 PM » |
|
It could cause problems ... but it may not.
Here's your potential problems:
1) Power surge, lightening strike, static electricity, voltage buildup and overcurrent damaging your gear (or you) because there's no way to de-energize the access or faulty circuit.
2) You reduce the ability to use the ground or lift the ground on your gear in order to reduce 60-cycle (60Hz) noise/hum ... or noise from other electrical devices in the home (e.g. fluorescent lighting, air conditioner, etc.).
There are other safety reasons to have grounded AC outlets, especially in a garage, but I'll leave it at that.
Personally, I would spend the money to ground your garage.
If the AC outlets don't physically have a ground, flip the breaker, remove the outlet from the gang box and look to see if the wiring has a ground wire there. If so, just replace outlets with ground AC outlets ... assuming the ground wiring actually runs to your breaker box and the ground wire is in fact grounded.
I installed my own grounding rod for my studio back in Dallas. It's easy to do, but you may need to hire a master electrician for safety reasons and/or city regulations. I have a strong background in electronics (long story) and have worked with many master electricians in my younger years (another long story), so I feel comfortable doing my own wiring and working with the breaker box.
I wouldn't risk it personally ... I'd have a ground put in. If it's an old house, you'll want the ground there at some point just to be able to sell at some point.
If you can, put some GFCI outlets in and make sure the breakers you do have for the garage will handle the amps you will be pulling. Since your garage isn't grounded, the breakers may not be rated very high ... like you would think.
|
|
|
|
|
Logged
|
My doctor says it's bad for my blood pressure if my mind is blown for more than five minutes at a time.
|
|
|
TMe
Gold Member
Offline
Posts: 787
I am evil Homer, I am evil Homer..!
|
 |
« Reply #2 on: August 06, 2008, 09:13 AM » |
|
Thanks Bart.
It turns out the receptacle box is not grounded, so no luck with that idea.
I think I'll test the amps and if the hum isn't too bad I'll just install GFCI outlets for safety.
I'm okay with replacing switches and outlets, but that's about as far as I go with electrical work.
Building code is pretty stringent in Ontario, especially for utilities, so I doubt any qualified electrician would want to touch the project without rewiring everything back to the panel, which is inside the house. That kind of work is outside of my budget.
|
|
|
|
|
Logged
|
"Some people say I ain't so super groovy. Why don't I leave the music alone?" Black Uhuru
|
|
|
boomerweps
supporter
Silver Member
Offline
Posts: 322
I love the Drummer Cafe!
|
 |
« Reply #3 on: August 06, 2008, 10:38 AM » |
|
Replacing the ungrounded wire from your garage to the Circuit breaker box isn't rocket science and should not cost too much (although copper has doubled over the last couple years, thank you China!). You really should have a SAFETY grounded source for garage work anyways.
You CAN run a heavy duty extension cable from a grounded outlet elsewhere. In USA terms, use a 12AWG cable. Having all the audio gear sharing the same ground, through a surge suppressor or a splitter box on the extension cord, will get rid of any differences in ground potential that cause MOST AC noise problems. For surge suppressors to work, they have to be able to discharge voltage through the safety ground.
Ground Fault Interupters (GFIs) are often enough incompatible with many surge suppressors. There are SOME GFIs available that will work with 2 wire ungrounded AC systems.
In the USA, just adding a ground rod is NOT enough. And there are specs for where and how long the ground rod must be. The grounding rod is for LIGHTENING protection of the building curuits.
Boomerweps
|
|
|
|
|
Logged
|
|
|
|
diddle
supporter
Gold Member
Online
Posts: 671
I love to play chess and sip coffee!
|
 |
« Reply #4 on: August 06, 2008, 12:00 PM » |
|
The necessity of the ground pin on an AC wall outlet is more about personnel safety... not equipment saftey.
|
|
|
|
|
Logged
|
|
|
|
Bart Elliott
Chef de Cuisine
Platinum Member
Online
Posts: 12772
Be Thankful
|
 |
« Reply #5 on: August 06, 2008, 12:29 PM » |
|
The necessity of the ground pin on an AC wall outlet is more about personnel safety... not equipment saftey.
Except that without a ground, some equipment will pick up and enhance 60Hz and other extraneous frequencies. Without a ground you have no choice to use or lift the ground on audio equipment (i.e. amps, direct boxes, etc.). Not having a ground as a choice can be a real pain. Having a ground can be a pain as well, which is why lifting it is sometimes necessary. Personally I'd rather have it there so I can choose. With no ground present, you have no choice or options available.
|
|
|
|
|
Logged
|
My doctor says it's bad for my blood pressure if my mind is blown for more than five minutes at a time.
|
|
|
Louis
Cafe VIP
Platinum Member
Online
Posts: 5878
Will Drum for BBQ
|
 |
« Reply #6 on: August 07, 2008, 06:14 PM » |
|
I think I'll test the amps and if the hum isn't too bad I'll just install GFCI outlets for safety. Those outlets will not work without a ground!
|
|
|
|
|
Logged
|
No one will believe it's the "Blues" if you wear a suit, 'less you happen to be an old person, and you slept in it last night!
|
|
|
Nick
Cafe VIP
Gold Member
Offline
Posts: 546
“It’s because you touch yourself at night... ”
|
 |
« Reply #7 on: August 09, 2008, 05:00 AM » |
|
If a re-wire is out of the question, I would be inclined to run a one or more extremely heavy duty extension cables from grounded sockets in the house... Obviously being careful of rating so you don’t over load socket or extension. Just a thought..  N
|
|
|
|
|
Logged
|
|
|
|
boomerweps
supporter
Silver Member
Offline
Posts: 322
I love the Drummer Cafe!
|
 |
« Reply #8 on: August 09, 2008, 03:02 PM » |
|
Those outlets will not work without a ground!
Sorry, Louis, not true. The GFI detects the difference in flow from the hot to the neutral/return, NOT the ground. The circuit design assumes any detectable flow DIFFERENCE from the hot supply to the Neutral return is running through a human and trips the interupter circuit. This is why any circuit that trickles ANY voltage to the safety ground, like SOME "power conditioners", trips the interupter. So you can buy and use GFIs with ungrounded systems. Boomerweps
|
|
|
|
|
Logged
|
|
|
|
Louis
Cafe VIP
Platinum Member
Online
Posts: 5878
Will Drum for BBQ
|
 |
« Reply #9 on: August 10, 2008, 09:55 AM » |
|
Sorry, Louis, not true. The GFI detects the difference in flow from the hot to the neutral/return, NOT the ground. I guess I should have phrased that better! The GFCI detects the difference as you noted however the NEC requires it to be installed with a ground. There were many updates concerning GFCIs in the 2005 and 2008 and lots of fine print notes specifically for GFCIs. I will agree that installing a GFCI without a ground is better in some cases is than not but consider the case of a guitar amp and a PA using the outlet with a GFCI installed without a ground. If one piece of equipment has a defect there is a possibility of potentially lethal voltage being present on the case of the equipment (or the guitar strings or mic housing) and if you touch the other piece of equipment the voltage has a path through your body. The GFCI will still see a balanced load on the hot and neutral and not exceed the 4 - 6 millamps needed to trip the breaker unless your body is grounded somewhere else. If A ground were present and the same fault developed the internal equipment grounding would give this fault current a path that would trip the breaker immediately and not pose a hazard.
|
|
|
|
|
Logged
|
No one will believe it's the "Blues" if you wear a suit, 'less you happen to be an old person, and you slept in it last night!
|
|
|
TMe
Gold Member
Offline
Posts: 787
I am evil Homer, I am evil Homer..!
|
 |
« Reply #10 on: August 11, 2008, 07:51 AM » |
|
Damned guitarists. Could this be natural selection at work?  Does the size of ampl make any difference to the amount of risk involved? We're using tiny amps, so would the potential shock be any less. I guess I have to weight the risk of electrocution from ungrounded power against the risk of running an extension cord. Another question (although I should probably be asking on a home remodelling forum); how do I check that the ground on an outlet is actually working? It turns out the second outlet in the garage is on a separate circuit and has a ground wire, but I'm not convinced it's actually doing anything.
|
|
|
|
|
Logged
|
"Some people say I ain't so super groovy. Why don't I leave the music alone?" Black Uhuru
|
|
|
Louis
Cafe VIP
Platinum Member
Online
Posts: 5878
Will Drum for BBQ
|
 |
« Reply #11 on: August 11, 2008, 05:19 PM » |
|
how do I check that the ground on an outlet is actually working? Go to home Depot or Lowes and buy an outlet tester. It cost a couple of bucks and has three LEDs. plug it in an outlet and use the markings on the side to see if the outlet is wired correctly and is grounded.
|
|
|
|
|
Logged
|
No one will believe it's the "Blues" if you wear a suit, 'less you happen to be an old person, and you slept in it last night!
|
|
|
Bart Elliott
Chef de Cuisine
Platinum Member
Online
Posts: 12772
Be Thankful
|
 |
« Reply #12 on: August 11, 2008, 05:49 PM » |
|
When I was a youngster, playing in my first bands, we had rehearsals in my garage. The outlets were not grounded, and the guitarist grabbed his guitar cable, already plugged into the amp, and proceeded to plug it into the guitar. What happened next ... he's shaking, unable to let go of the cable, shouting to the best of his ability (more like a faint whimper) ... "turn it off, turn it off".
It was funny after we realized there was no permanent damage, but he was definitely getting a charge, having grounded the amp with his body.
|
|
|
|
|
Logged
|
My doctor says it's bad for my blood pressure if my mind is blown for more than five minutes at a time.
|
|
|
Rich452
Bronze Member
Offline
Posts: 164
|
 |
« Reply #13 on: August 11, 2008, 07:13 PM » |
|
Go to home Depot or Lowes and buy an outlet tester. It cost a couple of bucks and had three LEDs. plug it in an outled and use the markings on the side to see if the outlet is wired correctly and is grounded.
Great advice, I am an Electrical Engineer and that would be the professional recommendation. Also, if you find an oulet problem, ungrounded, floating ground or neutral, hot and neutral wires reversed, consider calling a qualified electrician.
|
|
|
|
|
Logged
|
|
|
|
eardrum
Cafe VIP
Platinum Member
Online
Posts: 1331
It's not too late to get better!
|
 |
« Reply #14 on: August 12, 2008, 06:32 PM » |
|
People have died! Seriously!!! So I get a little sideways when someone says they want to save a few bucks. Get it done correctly and safely. Imagine I'm going to take you across country in my old car and knowing that the break fluid was leaking I decided to save some money and put some bubble bum on it (probably bought CDs instead). Do you really want to get in the car and tackle the Rockies, the Sierras, Mulholland Drive???
The stats are alarming.... just google "electrical shock injury lawyer". People make their living off these accidents. Don't mess with electricity.
|
|
|
|
|
Logged
|
|
|
|
TMe
Gold Member
Offline
Posts: 787
I am evil Homer, I am evil Homer..!
|
 |
« Reply #15 on: August 14, 2008, 10:36 AM » |
|
Go to home Depot or Lowes and buy an outlet tester. It cost a couple of bucks and has three LEDs. plug it in an outlet and use the markings on the side to see if the outlet is wired correctly and is grounded.
Thanks. I have such a device from my youth, and it only has two LED's. I didn't realize the newer ones test for ground as well. (Am I dating myself?)
|
|
|
|
|